It trips for no apparent reason and often when we are away so not due to toaster or kettle.
Socket ring main keeps tripping.
So as zax47 says it s most likely a general fault on the ring main that s tripping and causing your main rcd to trip.
Three reasons why circuit breaker keep tripping.
This occurs when you want a particular circuit to provide more electricity than its actual capacity.
An overloaded circuit is the most common reason for a circuit breaker tripping.
32amp mcb constantly tripping when no plug socket is in use.
Is this now a problem with the wiring.
It could just be a faulty mcb if you want to test it then swap it for the one same rating should be 32a that controls the upstairs ring main.
Only the main circuit breaker trips not the individual breakers.
It occurs when a circuit is attempting to draw a greater electrical load than it is intended to carry.
Call a pro to determine if a ground fault is why your circuit breaker keeps tripping.
Discussion in electricians.
Hi my friends house has all his sockets on one ring main with spurs added through out the house all of a sudden the mcb triped also causing the 80rcd to trip aswel split load board so we dissconected every socket in the house and belled.
A circuit overload is one of the main reasons why circuit breakers trip constantly.
This will lead to the overheating of the circuit which puts all the electrical appliances.
The electric keeps tripping out the downstairs sockets.
I have also changed the sockets for double pole ones and it still trips the rcd.
In the world of wiring any time an abnormal surge of electricity occurs it s known as a fault or a.
Electric keeps tripping our downstairs sockets.
Hi i have a ring mains for my downstairs sockets and very recently the circuit keeps tripping the rcd protecting it.